OSB SHEATHING SHRINKAGE CAUSING
STUCCO CRACKS ?
I got called to investigate a badly cracked
stucco
installation that appeared to have a very good Portland cement, lime
and
sand mix, was the right thickness, and was very durable and hard.
It was installed during the drought we experienced during last summer
and
fall by a very experienced and reputable stucco installation company.
The
general contractor is telling the stucco installer they must repair the
installation
and recoat the project at the installer's
expense.
As a building envelope consultant,
I want
to be fair to everyone involved and just deal with the conditions and
the
facts leading to those conditions.
After questioning the installer
concerning the
mixing of components, the experience of the particular crew, the crew's
supervision, how much water was used in the application of the three
coats,
keeping the installation sufficiently moist during curing during a
drought,
and examining the construction, I observed the following
conditions.
1. The upscale
residence had
a lumber package sent to the site and the wood framing and
completed
roofing were in place within two weeks of delivery to the site.
2. The construction is
wood
framing, 7/16" OSB sheathing and a Tyvek wrap, metal lath and the three
coat stucco installation with the finish coat applied in a skip-trowel
pattern.
3. The stucco installer
said
the Tyvek installation appeared to be adequate with good over lap and
good
coverage.
4. The stucco installer
said
the framer (the general contractor who is also the developer of the
subdivision)
installed the lath and nailed the lath approximately six to eight
inches
on center to the OSB sheathing. The OSB used for shingle roof
decking
has the proper spacing with metal spacer
clips
but the wall sheathing boards contact each other, do have spacing and
do
not have separator clips or spacer clips. Boards have buckled or
moved out of the plane of the wall along horizontal board
joints.
5. There are more good
window
and door corners than ones with reentrant cracks off of the apex of
those
corners.
6. Multiple cracks in the
pattern
of the wall wood framing are evident out from windows and wall corners,
and especially on what is the second story.
7. There is at
least
one distinctive circular crack in the stucco installation and the
stucco
is hard.
8. Cracks extend through
all
three coats and are much larger than hairline cracks in many places.
9. The stucco installer
stated
there were cracks in the interior drywall installation but I was not
able
to observe these because the house had been recently recaulked and
repainted.
10. A separate unattached
garage
has numerous cracks in walls and also few cracks off of windows and
doors.
Two wall corners have bad cracks right in the corner.
Please share your thoughts with
me. One
of your comments in the FAQ section
made reference to your preference for OSB
over
plywood because you had fewer
cracks. This is somewhat surprising
considering
the difference in the way OSB takes
on moisture and dries. Do you think
I'm
right in asking the general contractor to pay
for either the complete reworking of the
stucco
installation, or at least a preparation
coat and new flexible finish coat?
Thank you for your attention to this
e-mail and
to these requests.
In the last year and a half, I have
discovered
a method of keeping the cracks down to none
or
very
very few (two on one big house ,max) by
adding
plasticizers in the finish coat. It costs
me
about 50 cents
a square foot more, so I just charge
more.
I don't have to fight over
cracks
anymore.
This may even be a solution if a recoat is
done.
Typically, the worst cause of cracks
are:
flimsy or inadequate braced
framing.
Not allowing enough time for the
brown coat to cure before the finish.
We generally let it sit a week, or
at
least 3 days. This creates a lot of
cracks
due to abnormal shrinkage. If someone
won't
give me time, I simply turn down the
job.
I also insist the roof is finished or at
least
loaded down before we start,
Particularly
if it has a slate or Spanish tile
roof.
It sounds like probably that the framing
lumber
was way too green. If the walls have
shifted
badly out of plane this sounds most
likely
like the culprit. It probably came straight
from
the sawmill.
Or possibly abnormal expansion due to
the
dry/wet season.
If you can read the studs by the cracks,
this
is sounds like the reason. The
drywall
on
the inside shouldn't have cracks.
Usually, when plywood isn't
adequately
spaced, you can read the joints in the
plywood,
(or OSB).
I love OSB. I think OSB is better
because
it doesn't delaminate and warp like
plywood.
And it doesn't bounce like a
basketball
when you shoot staple or drive nails in
it.
It just seems to feel more solid. We
do
get fewer cracks. I think OSB tends
to
expand,
and plywood tends to shrink.
I think at this time you need to get the
finger
pointing out of the way and concentrate
on
constructive solutions.
A flexible finish coat is your easiest
ticket
out,
or painting with elastomeric paint, easier
yet.
It would be a solution for this
project,
but I doubt these materials are
breathable
like the manufacturers say. Another down
side
is that you lose the natural portland
cement
color, but
it will kill the cracks, and not use too
much
thickness.
I don't think the plastering contractor was
at
fault,
but I feel he should meet the builder part
way
on the
expense, particularly if he is an old or
repeat
customer,
or a real good payor. I would.
Maybe some lessons will be learned by
all here,
and everyone will still think positively
about
stucco,
a dying tradition I am trying to
preserve.
I hope all this helps. Write back if I
can
help.